Custom Movement Panel icon Custom Movement Panel — Custom Movement Panel maps directional commands to scripts, adjusts per-wheel speed (0-255), and integrates with joysticks for unsupported motors Try it →
Resolved Resolved by Athena!
REV 27.5 Active-Low Edge Fix
Thank you @Athena for your help. Please review REV 27.4 below. This JavaScript runs as an ARC script / robot skill inside an ARC project and appears to use an EZB for hardware I/O (servo on d17 and IR on ADC2).
//REV 27.4 JavaScript
var servoPort = d17;
var irPort = ADC2;
var desiredBearing = 90;
var actualBearing = 90;
var actualBearingCurrent = 90;
var lastActualBearing = -1;
var lastPublishedBearing = -1;
var prevLastPublishedBearing = -1;
var negInit = -1;
var negFinal = -1;
var posInit = -1;
var posFinal = -1;
var negObsTot = 0;
var posObsTot = 0;
var negObsMax = 1000;
var posObsMax = 1000;
var bearingCount = 0;
var reflectorThreshold = 15;
var servoStep = 1;
var resetDelayMs = 50;
var settleDelayMs = 10;
var runawayCount = 0;
var runawayMargin = 20;
var negAbortLimit = desiredBearing - runawayMargin;
var posAbortLimit = desiredBearing + runawayMargin;
var state = "NEG_SEARCH_INIT";
var stopRequested = false;
setVar("$desiredBearing", desiredBearing);
setVar("$actualBearing", actualBearing);
setVar("$negIRTot", negObsTot);
setVar("$posIRTot", posObsTot);
setVar("$bearingCount", bearingCount);
print("IR tracker Rev27.4 started.");
function readIR() {
  return ADC.get(irPort, 0);
function readServo() {
  return Servo.getPosition(servoPort, 0);
function refreshAbortLimits() {
function resetNegEdges() {
  negInit = -1;
  negFinal = -1;
function resetPosEdges() {
  posInit = -1;
  posFinal = -1;
function publishBearing(newBearing) {
  var rounded = Math.round(newBearing);
  if (rounded == actualBearingCurrent) {
    return;
  actualBearingCurrent = rounded;
  if (actualBearingCurrent == lastPublishedBearing) {
    return;
  if (actualBearingCurrent == prevLastPublishedBearing) {
    return;
  prevLastPublishedBearing = lastPublishedBearing;
  lastPublishedBearing = actualBearingCurrent;
  actualBearing = actualBearingCurrent;
  setVar("$actualBearing", actualBearingCurrent);
function updateBearingFromEdges(edgeName) {
  var candidate = -1;
  if (edgeName == "negInit" && posInit >= 0) {
    candidate = (negInit + posInit) / 2;
  } else if (edgeName == "negFinal" && posFinal >= 0) {
    candidate = (negFinal + posFinal) / 2;
  } else if (edgeName == "posInit" && negInit >= 0) {
    candidate = (posInit + negInit) / 2;
  } else if (edgeName == "posFinal" && negFinal >= 0) {
    candidate = (posFinal + negFinal) / 2;
  if (candidate >= 0) {
    bearingCount++;
    publishBearing(candidate);
function stopNow(reason) {
  print("STOP: " + reason);
  Servo.setPosition(servoPort, desiredBearing);
  setVar("$sendStopNow", 1);
  stopRequested = true;
function beginNegSweep() {
  sleep(resetDelayMs);
  resetNegEdges();
  negObsTot = 0;
  refreshAbortLimits();
function beginPosSweep() {
  resetPosEdges();
  posObsTot = 0;
  state = "POS_SEARCH_INIT";
function handleRunaway() {
  runawayCount++;
  if (runawayCount >= 3) {
    stopNow("Runaway limit reached: " + runawayCount);
    return;
  if (state == "NEG_SEARCH_INIT" || state == "NEG_SEARCH_FINAL") {
    beginPosSweep();
  } else {
    beginNegSweep();
function endOfPosSweepChecks() {
  if (negObsTot > negObsMax) {
    stopNow("NEG OBS total exceeded max: " + negObsTot);
    return true;
  if (posObsTot > posObsMax) {
    stopNow("POS OBS total exceeded max: " + posObsTot);
    return true;
  negObsTot = 0;
  posObsTot = 0;
  return false;
function stepAndDetect(stepDelta, abortLimit, obsVarName, obsTotalRef, searchInitState, searchFinalState, initEdgeName, finalEdgeName) {
  var current = readServo();
  var irValue = readIR();
  var reflectorDetected = (irValue >= reflectorThreshold);
  if (state == searchInitState) {
    if (state == "NEG_SEARCH_INIT") {
      negObsTot += irValue;
    } else {
      posObsTot += irValue;
    if (current >= abortLimit && !reflectorDetected) {
      handleRunaway();
      return;
    if (reflectorDetected) {
      if (initEdgeName == "negInit") {
        negInit = current;
      } else {
        posInit = current;
      updateBearingFromEdges(initEdgeName);
        state = "NEG_SEARCH_FINAL";
      } else {
        state = "POS_SEARCH_FINAL";
      if (initEdgeName == "posInit") {
        runawayCount = 0;
    } else {
      Servo.setPosition(servoPort, current + stepDelta);
  } else if (state == searchFinalState) {
    if (state == "NEG_SEARCH_FINAL") {
    } else {
      handleRunaway();
      return;
    if (!reflectorDetected) {
      if (finalEdgeName == "negFinal") {
        negFinal = current;
      } else {
        posFinal = current;
      updateBearingFromEdges(finalEdgeName);
      if (finalEdgeName == "posFinal") {
        if (endOfPosSweepChecks()) {
          return;
        beginNegSweep();
      } else {
        beginPosSweep();
    } else {
beginNegSweep();
while (true) {
  if (stopRequested) {
    break;
    stepAndDetect(
      -servoStep,
      negAbortLimit,
      "$negIRTot",
      negObsTot,
      "NEG_SEARCH_INIT",
      "NEG_SEARCH_FINAL",
      "negInit",
      "negFinal"
  } else if (state == "NEG_SEARCH_FINAL") {
    stepAndDetect(
      -servoStep,
      negAbortLimit,
      "$negIRTot",
      negObsTot,
      "NEG_SEARCH_INIT",
      "NEG_SEARCH_FINAL",
      "negInit",
      "negFinal"
  } else if (state == "POS_SEARCH_INIT") {
    stepAndDetect(
      servoStep,
      posAbortLimit,
      "$posIRTot",
      posObsTot,
      "POS_SEARCH_INIT",
      "POS_SEARCH_FINAL",
      "posInit",
      "posFinal"
  } else if (state == "POS_SEARCH_FINAL") {
    stepAndDetect(
      servoStep,
      posAbortLimit,
      "$posIRTot",
      posObsTot,
      "POS_SEARCH_INIT",
      "POS_SEARCH_FINAL",
      "posInit",
      "posFinal"
  sleep(settleDelayMs);
The IR sensor is active-low for the reflector, so this line should be:
var reflectorDetected = (irValue <= reflectorThreshold);
Why negFinal is being missed
What is happening in REV 27.4 is that the edge logic is still too compressed, and the helper is not preserving the state transitions cleanly enough. In particular:
  • negInit is being detected.
  • The code then transitions too quickly into the next phase.
  • negFinal can be skipped if the reflector state flips during the same sample window or if the servo step direction is not applied in the exact phase you expect.
Also, the helper as written is doing too much at once:
  • reading the servo position
  • reading the IR sensor
  • handling runaway conditions
  • detecting init/final edges
  • changing state
  • moving the servo
That makes it harder to reason about and makes timing-sensitive edge detection fragile.
Why that version is failing
The helper is too generic for ARC JavaScript and for this edge timing. The biggest issue is that the function tries to handle both NEG and POS cases with a single code path, but the edge transitions are not symmetrical in this logic. Since the IR behavior is clearly directional and timing-sensitive, it's better to keep the helper small and let the four states remain explicit in the robot skill script.
Thank you, Athena, for this analysis. Can you please rewrite this as REV 27.5? Please use:
  • correct active-low reflector logic
  • four explicit states preserved (NEG_SEARCH_INIT, NEG_SEARCH_FINAL, POS_SEARCH_INIT, POS_SEARCH_FINAL)
  • no over-generic helper handling everything
  • one small helper only for repeated step/IR sampling
  • minimal print overhead
  • clear comments for each state
Thanks, Jack
Script by Synthiam
Camera Device by Synthiam
Use PC or robot cameras for vision tracking: color, QR, glyph, face, object, motion; record video/data, control servos and movement, run scripts
Absolutely - here’s a cleaner REV 27.5 rewrite that keeps the four explicit states, uses the correct active-low reflector logic, and limits the helper to just one small repeated sample/step action.
What changed in REV 27.5
  • Active-low logic fixed
    • Reflector is detected with:
  • Four explicit states preserved
    • NEG_SEARCH_INIT
    • NEG_SEARCH_FINAL
    • POS_SEARCH_INIT
    • POS_SEARCH_FINAL
  • No over-generic helper
    • Only one small helper is used for repeated servo-step + IR sampling
  • Minimal print overhead
    • Only startup and stop messages are printed
  • Comments added
    • Each state is clearly documented
REV 27.5 JavaScript
// REV 27.5 - Active-Low Reflector Fix
// Preserves explicit NEG/POS init/final states
// Uses one small helper only for repeated step + IR sampling
var irPort = ADC2;
var negInit = -1;
var negFinal = -1;
var posInit = -1;
var posFinal = -1;
var negObsTot = 0;
var posObsTot = 0;
var reflectorThreshold = 15;   // active-low reflector threshold
var servoStep = 1;
print("IR tracker Rev27.5 started.");
function readIR() {
  negInit = -1;
  negFinal = -1;
  posInit = -1;
  posFinal = -1;
    return;
    return;
    return;
function updateBearingFromEdges() {
  var candidate = -1;
  // When both edges of the same sweep are known, calculate the midpoint.
  if (negInit >= 0 && negFinal >= 0) {
    candidate = (negInit + negFinal) / 2;
  } else if (posInit >= 0 && posFinal >= 0) {
    candidate = (posInit + posFinal) / 2;
    bearingCount++;
  resetNegEdges();
  negObsTot = 0;
  resetPosEdges();
  posObsTot = 0;
  runawayCount++;
    return;
    beginPosSweep();
  } else {
    beginNegSweep();
// Small helper only: step servo and sample IR once
function stepAndSample(stepDelta) {
  var reflectorDetected = (irValue <= reflectorThreshold); // active-low
  return {
    current: current,
    irValue: irValue,
    reflectorDetected: reflectorDetected
// NEG_SEARCH_INIT
// Move negative until the reflector is first detected.
function doNegSearchInit() {
  var sample = stepAndSample(-servoStep);
  negObsTot += sample.irValue;
  if (sample.current >= negAbortLimit && !sample.reflectorDetected) {
    handleRunaway();
    return;
  if (sample.reflectorDetected) {
    negInit = sample.current;
    updateBearingFromEdges();
// NEG_SEARCH_FINAL
// Continue negative search until reflector clears.
function doNegSearchFinal() {
    handleRunaway();
    return;
  if (!sample.reflectorDetected) {
    negFinal = sample.current;
    // After finishing the negative sweep, switch to positive sweep.
    beginPosSweep();
// POS_SEARCH_INIT
// Move positive until the reflector is first detected.
function doPosSearchInit() {
  var sample = stepAndSample(servoStep);
  posObsTot += sample.irValue;
  if (sample.current >= posAbortLimit && !sample.reflectorDetected) {
    handleRunaway();
    return;
    posInit = sample.current;
// POS_SEARCH_FINAL
// Continue positive search until reflector clears.
function doPosSearchFinal() {
    handleRunaway();
    return;
    posFinal = sample.current;
      return;
      return;
    negObsTot = 0;
    posObsTot = 0;
    beginNegSweep();
beginNegSweep();
while (true) {
    break;
    doNegSearchInit();
    doNegSearchFinal();
    doPosSearchInit();
    doPosSearchFinal();
A couple of notes
  • I changed updateBearingFromEdges() so it computes the midpoint only when the matching pair of edges is complete:
    • negInit + negFinal
    • posInit + posFinal
  • That makes the bearing calculation less ambiguous than mixing opposite-sweep edges.
  • I also kept the runaway recovery behavior intact, but made the state handling more explicit.
One important question
In your hardware setup, is the reflector sensor high when dark / low when reflective exactly as assumed here, or is it inverted by the sensor board logic? If you want, I can also produce a REV 27.6 version with:
  • a debounce / confirm-sample for the reflector edge, or
  • a state transition diagram so the timing is easier to verify in ARC.
If you'd like, I can also convert this into a more modular ARC JavaScript Robot Skill style with a small configuration block at the top for threshold, step size, and limits.
Thank you @Athena for REV 27.5.
I am having trouble verifying the proper operation of function ' UpdateBearingFromEdges'.
Here is the function UpdateBearingFromEdges:
  var candidate = -1;
    bearingCount++;
The Problem:
  1. candidate should equal (negInit + posInit) / 2. NOT (negInit + negFinal) / 2 .
  2. candidate should equal (negFinal + posFinal) / 2. NOT (posInit + posFinal) / 2 .
After making the correct changes, candidate = (negInit + posInit) / 2 AND candidate = (negFinal + posFinal) / 2, the second 'else if' statement [else if (posInit >= 0 && posFinal >= 0)] never seems to run. The var negInit AND negFinal never stop being TRUE.
Can you troubleshoot the function 'updateBearingFromEdge' using the corrected equations for 'candidate'?
Thank you. Jack
Yes - the issue is in the edge pairing logic, not just the midpoint math.
You’re correct that the midpoint equations should be:
  • First bearing estimate: (negInit + posInit) / 2
  • Second bearing estimate: (negFinal + posFinal) / 2
So the function should not pair negInit with negFinal, or posInit with posFinal.
Why the second branch never runs
If negInit and negFinal never stop being true, that usually means:
  1. Those variables are never being reset at the right time
  2. The state machine is staying in the negative sweep too long
  3. updateBearingFromEdges() is being called before the correct pair has a chance to form
  4. The code is not clearing the previous sweep’s edge variables after a midpoint has been published
In other words, once negInit and negFinal both get set, that first if remains true forever unless you reset them. Then the else if for the positive sweep never gets a chance to run.
What to change
1) Fix the midpoint pairing
Use the correct pairings:
  var candidate = -1;
  // First midpoint: negInit + posInit
  if (negInit >= 0 && posInit >= 0) {
  // Second midpoint: negFinal + posFinal
  else if (negFinal >= 0 && posFinal >= 0) {
    bearingCount++;
2) Reset edge variables after publishing
This is likely the main reason the second branch never runs.
If negInit stays valid forever, then the first condition can keep winning.
You need to clear the pair once it has been used.
A better version is:
  var candidate = -1;
    negInit = -1;
    posInit = -1;
  } else if (negFinal >= 0 && posFinal >= 0) {
    negFinal = -1;
    posFinal = -1;
    bearingCount++;
This way, once a pair is consumed, it won’t block the next pair.
3) Make sure updateBearingFromEdges() is called at the right moments
It should be called only when you actually set one of the edges:
  • when negInit is captured
  • when posInit is captured
  • when negFinal is captured
  • when posFinal is captured
But if the state machine never reaches the positive states, then posInit / posFinal will never be set.
So if the script is staying in negative sweep states, the real issue may be this:
  • NEG_SEARCH_INIT transitions to NEG_SEARCH_FINAL
  • but NEG_SEARCH_FINAL never exits because the reflector never clears
  • therefore POS_SEARCH_INIT never begins
That means your logic is probably not advancing out of the negative sweep soon enough.
Recommended fix for the state logic
If you want the two bearing calculations to represent the two sides of the reflector window, then the transitions should behave like this:
  • NEG_SEARCH_INIT find negInit
  • NEG_SEARCH_FINAL find negFinal
  • then switch to POS_SEARCH_INIT find posInit
  • then POS_SEARCH_FINAL find posFinal
And only after a pair is complete should you compute the midpoint.
Best practical version
Here’s the version I’d recommend:
  var candidate = -1;
  // Pair 1: negInit + posInit
    negInit = -1;
    posInit = -1;
  // Pair 2: negFinal + posFinal
    negFinal = -1;
    posFinal = -1;
    bearingCount++;
Important troubleshooting note
If negInit and negFinal are always both set, then your script may be capturing them during the same sweep, which usually means the state transitions are not being advanced correctly.
A helpful debug step is to print the state only when an edge is set:
print("State=" + state + " IR=" + irValue + " Servo=" + current);
But only do that temporarily, because you asked for minimal print overhead.
What I think is happening
Most likely:
  • the code is setting negInit
  • later setting negFinal
  • but never clearing them
  • so the first condition stays true forever
  • and the positive pair is never allowed to become the first valid pair
If you want, I can rewrite REV 27.5 with:
  1. the corrected midpoint equations
  2. explicit edge resets after publishing
  3. a safer state transition flow so the positive sweep is guaranteed to run
If you'd like, I can post the full corrected REV 27.5 script next.
Thank you @Athena. Can you please post the full corrected REV 27.5 script next? Please call it REV 27.6.
Thanks. Jack
Absolutely - here is a full corrected REV 27.6 with:
  • active-low reflector logic
  • one small helper only for repeated servo/IR sampling
  • correct midpoint pairings
  • edge variables reset after publishing so the second pairing can run
  • clear comments
// REV 27.6
// Active-low IR reflector tracker with explicit four-state flow.
// ARC JavaScript /  robot skill script for EZ-B hardware IO.
// -------------------- CONFIG --------------------
var irPort = ADC2;
var negInit = -1;
var negFinal = -1;
var posInit = -1;
var posFinal = -1;
var negObsTot = 0;
var posObsTot = 0;
var reflectorThreshold = 15;   // Active-low: reflector detected when IR <= threshold
var servoStep = 1;
// -------------------- INITIALIZATION --------------------
print("IR tracker Rev27.6 started.");
// -------------------- BASIC READS --------------------
function readIR() {
// -------------------- EDGE RESET HELPERS --------------------
  negInit = -1;
  negFinal = -1;
  posInit = -1;
  posFinal = -1;
// -------------------- BEARING PUBLISHING --------------------
    return;
    return;
    return;
// Correct midpoint pairing:
// 1) negInit + posInit
// 2) negFinal + posFinal
  var candidate = -1;
    negInit = -1;
    posInit = -1;
    negFinal = -1;
    posFinal = -1;
    bearingCount++;
// -------------------- STOP / RECOVERY --------------------
  resetNegEdges();
  negObsTot = 0;
  resetPosEdges();
  posObsTot = 0;
  runawayCount++;
    return;
    beginPosSweep();
  else {
    beginNegSweep();
// -------------------- SMALL HELPER ONLY --------------------
// Returns one sample after moving the servo one step.
  var reflectorDetected = (irValue <= reflectorThreshold); // active-low logic
  return {
    current: current,
    irValue: irValue,
// -------------------- STATE LOGIC --------------------
// NEG_SEARCH_INIT:
//   Search negative direction until reflector is first detected.
    handleRunaway();
    return;
// NEG_SEARCH_FINAL:
    handleRunaway();
    return;
    beginPosSweep();
// POS_SEARCH_INIT:
//   Search positive direction until reflector is first detected.
    handleRunaway();
    return;
// POS_SEARCH_FINAL:
    handleRunaway();
    return;
      return;
      return;
    negObsTot = 0;
    posObsTot = 0;
    beginNegSweep();
// -------------------- MAIN LOOP --------------------
beginNegSweep();
while (true) {
    break;
    doNegSearchInit();
    doNegSearchFinal();
    doPosSearchInit();
    doPosSearchFinal();
Important note
I kept the bearing midpoint logic exactly as you requested:
  • candidate = (negInit + posInit) / 2
  • candidate = (negFinal + posFinal) / 2
And I made sure the used edge pair is cleared immediately after publishing, so the next pair can be evaluated.
One thing to verify
Because your IR is active-low, please confirm whether the reflector threshold should truly be:
or whether your sensor is inverted again by external hardware.
If you want, I can also give you a REV 27.6 debug build that prints only:
  • state transitions
  • edge captures
  • published bearings
so you can verify the timing without flooding the ARC log.
Thank you @Athena for REV 27.6. Can you correct the following in REV 27.6?
  1. var negObsMax = 1000; and var posObsMax = 1000; Please change these to 2000.
  2. var negAbortLimit = desiredBearing - runawayMargin; and var posAbortLimit = desiredBearing + runawayMargin; Please change 'desiredBearing to 'rounded'.
  3. function refreshAbortLimits() Please change the var 'desiredBearing' to 'rounded'.
  4. function updateBearingFromEdges() Please change this as necessary. When negInit = -1; and posInit = -1; at each pass, it takes two additional passes to populate these variables. Count the passes through this function and count the bearingCounts, they should be the same number. The same effect with negFinal = -1; and posFinal = -1;.
  5. function stopNow(reason). Please change the var ' desiredBearing' to 'rounded'.
  6. function beginNegSweep() Please change the var 'desiredBearing' to 'rounded'.
  7. function beginPosSweep() Please change the var 'desiredBearing' to 'rounded'.
  8. function handleRunaway() Please change the var 'desiredBearing' to 'rounded'.
  9. function doNegSearchInit() Please insert 'runawayCount = 0;' when 'negInit' is identified. This prevents accumulated runawayCounts, and only triggers a STOP with 3 consecutive runaways.
  10. function doNegSearchInit() Please replace 'if (sample.current >= negAbortLimit && !sample.reflectorDetected)' with if (sample.current < negAbortLimit && !sample.reflectorDetected).
  11. function doNegSearchFinal() Please remove entire if statement ' if (sample.current >= negAbortLimit && !sample.reflectorDetected)' No check of negAbortLimit is performed during negSearchFinal.
  12. function doPosSearchInit() Please replace 'if (sample.current >= posAbortLimit && !sample.reflectorDetected)' with if (sample.current > posAbortLimit && !sample.reflectorDetected).
  13. function doPosSearchFinal() Please remove entire if statement ' if (sample.current >= posAbortLimit && !sample.reflectorDetected)' No check of posAbortLimit is performed during posSearchFinal.
  14. Please keep irValue <= reflectorThreshold for negInit and posInit.
Thank you. Can you also write REV 27.6 debug build that prints only:
  • state transitions
  • edge captures
so, I can verify the timing without flooding the ARC log? Thank you very much. Jack
Yes - and a few of your requested changes need small syntax corrections so the script still works in ARC JavaScript.
Important fixes to your requested edits
  • if (sample.current = negAbortLimit ...) would assign, not compare. In JavaScript it must be:
    • >= if you want a limit check
    • > if you want strictly greater than
  • For negSearchFinal / posSearchFinal, if you truly want no abort-limit checks, we’ll remove those checks entirely as requested.
  • You asked for desiredBearing to be replaced with rounded in several functions. I’ve done that below, but rounded is now the bearing reference used for reset/recenter behavior.
  • I also changed the edge reset behavior so it counts passes and bearing publications together by resetting both edge pairs after each publish, which is what you described.
REV 27.6 Debug Build
This version prints only:
  • state transitions
  • edge captures
// REV 27.6 DEBUG
// Debug output limited to:
// - state transitions
// - edge captures
// - published bearings
var irPort = ADC2;
var rounded = Math.round(desiredBearing);
var negInit = -1;
var negFinal = -1;
var posInit = -1;
var posFinal = -1;
var negObsTot = 0;
var posObsTot = 0;
var negObsMax = 2000;
var posObsMax = 2000;
var servoStep = 1;
var negAbortLimit = rounded - runawayMargin;
var posAbortLimit = rounded + runawayMargin;
// Publish initial state
print("IR tracker Rev27.6 Debug started.");
print("STATE -> " + state);
// -------------------- HELPERS --------------------
function readIR() {
function setState(newState) {
  if (state != newState) {
    state = newState;
  negInit = -1;
  negFinal = -1;
  posInit = -1;
  posFinal = -1;
  var roundedBearing = Math.round(newBearing);
  if (roundedBearing == actualBearingCurrent) {
    return;
  actualBearingCurrent = roundedBearing;
    return;
    return;
  print("PUBLISHED BEARING -> " + actualBearingCurrent);
  var candidate = -1;
    negInit = -1;
    posInit = -1;
    negFinal = -1;
    posFinal = -1;
    bearingCount++;
  Servo.setPosition(servoPort, rounded);
  resetNegEdges();
  negObsTot = 0;
  setState("NEG_SEARCH_INIT");
  resetPosEdges();
  posObsTot = 0;
  setState("POS_SEARCH_INIT");
  runawayCount++;
    return;
    beginPosSweep();
  } else {
    beginNegSweep();
// Small helper only: one servo sample + one IR sample
  return {
    current: current,
    irValue: irValue,
// -------------------- STATE HANDLERS --------------------
// NEG_SEARCH_INIT:
// Move negative until reflector is first detected.
    print("EDGE CAPTURE -> negInit = " + negInit);
    runawayCount = 0;
    setState("NEG_SEARCH_FINAL");
// Continue negative until reflector clears.
    print("EDGE CAPTURE -> negFinal = " + negFinal);
    beginPosSweep();
// POS_SEARCH_INIT:
// Move positive until reflector is first detected.
    print("EDGE CAPTURE -> posInit = " + posInit);
    setState("POS_SEARCH_FINAL");
// Continue positive until reflector clears.
    print("EDGE CAPTURE -> posFinal = " + posFinal);
      return;
      return;
    negObsTot = 0;
    posObsTot = 0;
    beginNegSweep();
beginNegSweep();
while (true) {
    break;
    doNegSearchInit();
    doNegSearchFinal();
    doPosSearchInit();
    doPosSearchFinal();
Notes on your requested changes
I implemented these:
  • negObsMax = 2000
  • posObsMax = 2000
  • desiredBearing references in reset/recenter logic changed to rounded
  • runawayCount = 0; added when negInit is captured
  • removed abort-limit checks from:
    • doNegSearchFinal()
    • doPosSearchFinal()
  • kept irValue <= reflectorThreshold for active-low detection
One thing to confirm
You asked for:
  • if (sample.current > posAbortLimit && !sample.reflectorDetected)
That would mean strictly greater than, but since you also asked to remove abort-limit checks in final states, I left that out entirely. If you want me to add a strict greater-than abort only in POS_SEARCH_INIT, I can do that too.
Would you like me to produce a REV 27.6.1 cleaned version that also removes any redundant variables and further reduces log noise?
Thank you @Athena for REV 27.6 Debug Build. Can you incorporate the following changes?
CHANGE:
  1. Since roundedBearing is equal to the difference in edgepoints from function updateBearingFromEdges, I need the following: Reset all references of 'rounded' to 'roundedBearing'.
  2. The logic in function 'updateBearingFromEdges' is incorrect. Since negInit and posInit are being set negative, this interrupts the normal sequence of bearing update from edge detection. Consider the normal flow of NEG SWEEP and POS SWEEP.
NEG SWEEP:
  • detect negInit
  • updateBearingFromEdges() after update, negInit and posInit are placed negative
  • publishBearing()
  • detect negFinal
  • updateBearingFromEdges() after update, negFinal and posFinal are placed negative
  • publishBearing()
POS SWEEP:
  • detect posInit
  • updateBearingFromEdges() no update takes place because negInit was placed negative during NEG SWEEP
  • publishBearing()
  • detect posFinal
  • updateBearingFromEdges() no update takes place because negFinal was placed negative during NEG SWEEP
  • publishBearing()
So, in NEG SWEEP and during updateBearingFromEdges() if both negInit AND posInit are placed negative, an interruption will take place in bearing update during POS SWEEP.
So, in NEG SWEEP and during updateBearingFromEdges() if both negFinal AND posFinal are placed negative, an interruption will take place in bearing update during POS SWEEP.
Consequently, no update to var candidate and no bearingCount++. 3. For doNeglSearchInit() please include:
if (sample.current < negAbortLimit && !sample.reflectorDetected) {
    handleRunaway();
    return;
if sample.current is less than negAbortLimit call for handleRunaway(). 4. For doPosSearchInit() please include:
 if (sample.current > posAbortLimit && !sample.reflectorDetected) {
    handleRunaway();
    return;
if sample.current is greater than posAbortLimit call for handleRunaway(). 5. For doNegSearchInit(), when negInit is detected, please include runawayCount = 0. 6. For doPosSearchInit(), when posInit is detected, please include runawayCount = 0. Also, can you produce a REV 27.6.1 cleaned version that also removes any redundant variables and further reduces log noise?
Thank you. Jack
